If they were surface mounted then no fill restrictions and no derating if under
2' long.
Pierre, Look at the panels closely. There is a gap between the wall and back box and no mounting screws through the back, making this a CSI break through. The panels are not surface mounted, they are side mounted. Hoosgottaredsticker.As the picture stands, this is not a violation as the panels are surface mounted.
.
A paradox? In the NEC? Say it's not so.
And the wall will be drywalled.
312.5(C)(g) says "where installed as conduit or tubing, the allowable cable fill does not exceed that permitted for complete conduit or tubing systems by Table 1 Chapter 9 of this and all applicable notes thereto".
Table 1 Chapter 9 Note (2): Table 1 applies only to complete conduit or tubing systems and is not intended to apply to sections of conduit or tubing used to protect exposed wiring from physical damage."
I would argue that an 18" to 24" "nipple" or "sleeve" does not count as a conduit system and is therefore excluded from applying the conduit fill rules of Table 1 Chapter 9.
Not that I would suggest cramming them full, but I believe them exempted on purpose by the wording of 312.5(C)(g). If they were connected to a trough or box then they would not be exempted because they may be interpreted as "complete systems".
This installation would not comply with 312.5(C) at all. In Western Kentucky this would never fly.
Have you ever see a fire that started in the panel with these stove pipes installed (as we call them in KY...... please, no comments on the NCAA) that are not sealed or plugged. Flames shoot out the top like a blow torch.
1. As per the [exception], the panels are mounted on the surface, as there is no surface that they are flush with.
Can I see or access the exterior sides of the panel?
It is defined by " no access to exterior sides of the panel".
The panels were put in after the stud wall was built making them recessed no matter what the reveal is. If the walls were put in after, Pierre would have a point.Honestly as an inspector I think Pierre could call that surface if he wanted to I just don't see it that way.:smile:
Pierre i have to disagree with you on this for discussion purposes. The panels have the required finished reveal already set. With your reasoning i could set a panel with a 1" reveal and use 1/2" finish board and call it surface mounted.1. As per the [exception], the panels are mounted on the surface, as there is no surface that they are flush with.
.
Here is a replay from a member of the CMP regarding 312.5(C). As you can see he is also from Kentucky (stovepipe).
I had always thought this was pretty clear. If the stovepipe is no more than 24" then the 60% rule applies from Chapter 9 Table 1 applies. If it is over 24", then you have to comply with the normal 40% fill rules.
Derating factors apply also when you get over 24".
Remember that tables apply as referenced from the Chapters. Since 312.5 specifically points you to use Chapter 9 Table 1, the statement in Note 2 saying only full conduit systems is nullified.
Here is a replay from a member of the CMP regarding 312.5(C). As you can see he is also from Kentucky (stovepipe).
I had always thought this was pretty clear. If the stovepipe is no more than 24" then the 60% rule applies from Chapter 9 Table 1 applies. If it is over 24", then you have to comply with the normal 40% fill rules.
Derating factors apply also when you get over 24".
Remember that tables apply as referenced from the Chapters. Since 312.5 specifically points you to use Chapter 9 Table 1, the statement in Note 2 saying only full conduit systems is nullified.