fisherelectric
Senior Member
- Location
- Northern Va
I really hate this language used in (g).
I would like to hear opinions of the language in the begining "Where installed as conduit or tubing..." It seems to qualify the raceway but what exactly does it mean?
I would take that to mean where the raceway is conduit or tubing you must apply the fill rules of Table1 Chap 9 and the " notes thereto". From Note 2: for "sections of conduit or tubing used to protect exposed wiring from physical damage" the Table need not be applied. If it were a complete system (terminated on both ends) then Table 1 would apply. Note 4 covers nipples less than 24" and which "are installed between boxes, cabinets, and similar enclosures" and permits 60% fill.