Romex in PVC pipe ?

Status
Not open for further replies.

ronaldsax

Member
Hi , I'm hoping that I can get help in this forum. a few questions that I have are.
can I pull Romex 14-2 in a 1/2" PVC pipe that goes underground?
do I need 2 grounding electrodes at the meter?.
well , any help will be really apreciated.

thank you very much
 
ronaldsax said:
Hi , I'm hoping that I can get help in this forum. a few questions that I have are.
can I pull Romex 14-2 in a 1/2" PVC pipe that goes underground?

No, you can not pull NM in an underground conduit, you can use UF though.


ronaldsax said:
do I need 2 grounding electrodes at the meter?.
well , any help will be really apreciated.
thank you very much

If a rod type GE is the sole GE and you don't want to prove 25 ohms or less, the answer is yes.

Roger
 
334.12(B) NM not permitted in damp or wet areas.
Article 100: Location, wet: Installations under ground.
300.5(B) Listing. Cables and insulated conductors installed in enclosures or raceways in underground installations shall be listed for use in wet locations.
 