jumper
- 3 Hr 2 Min from Winged Horses
sometimes.....
but then 310.15A2 exception would apply
~RJ~
Somewhat tricky IME. I do not like to ever try and use that section. Seems to irritate inspectors, not worth it to me most times.
sometimes.....
~RJ~
Pictures are helping me learn the code a bit easier, especially the ones like the article 100 definitions that show the different terms in relationship to each other, or the ones that tell me to refer to specific tables when calculating.. think I have a load of them on my laptop, along with the 2005 and 1980 something electrical codes... and three of the British codes as well..
loads to learn but, like Ham Radio, it is just learning the terms and learning to do the math fast enough for the tests... main thing seems to be getting used to flipping through the books to find the right info for the equations... so, will get there.
it is funny, as a handyman, thought all an electrician did was what they paid me to help them with and drink more coffee than me... pulling wire, stapling, drilling holes, placing the boxes... did not think about all the design stuff you guys had to learn...
That exception probably isn't as useful as one may want it to be though, especially in a dwelling.sometimes.....
~RJ~
Yes. I will say this is something I do sometimes see getting overlooked to some extent, but still there is rules for this situation.so that means the number of wires in a trough still have a limit due to ampacity, even if that trough is only three feet long, from the top of the breaker panel box to the ceiling area, before going to conduits? That rules out my idea uf running the conduits from the kitchen and living room into a trough coming down the wall... only 42 feet..lol...
Not that I was really going to do that but was trying to figure if it would have been easier than all the conduit bends...
so, if there is a rule against running romex in a sleeve except if the panel box is surface mounted and you do not run the sleeve into a permenant cieling, what about running romex in a conduit? Or am I confusing terms again ?
Raceway. An enclosed channel designed expressly for holding
wires, cables, or busbars, with additional functions as permitted
in this Code. (CMP-8)
Then you need a new inspector
~RJ~
ah, stout fellow! up the regiment...!~RJ~
Try applying it to these units, I wired 98 of these units for the Army.:
I remember seeing those on the news......flames going everywhere!![]()
Shush...those were the latrine/shower units.
I never worked on them except as a fill in sparky, my units were properly set up and bonded.
The people who did know the difference between an SDS and non SDS caused that.
So...![]()
Ok..thanks. Still confused but think I am starting to understand... so using a conduit or pipe as a bushing but longer is not ok for this product but, running a trough or a three inch conduit from one panel to a pull box or another panel is ok... running Romex in it allowed.. because it is a raceway not just a sleevetwo distinctions apply Adam
first, short runs can be used to protect romex, the shortest run sold in 10' long
second , and more importantly, a 'raceway' is defined in the NEC ('17) as
key word being 'enclosed' , meaning terminated in JB's and/or electrical enclosures at each end.
otherwise, it is NOT a raceway
it is considered a 'sleeve' or protective sleeve
~RJ~
Yes it does, I was just pointing out that quite often it isn't all that easy to meet the conditions unless you have long circuit runs. Then when you do have long runs the chance of increased conductor size for voltage drop may start to kick in and helps out with ampacity adjustments anyhow.the exception stands ,if one can prove it true kwired
~RJ~