I am lost, they always need to be supported unless fished and they always need to be secured.Originally posted by jbwhite:
In the above quoted section i did not see any wording that suggestes that they can not be supported if they are X distance away from the framing member. they are parallel, that is it, they need to be supported.
To which I replied it does not apply to the wires perpendicular to the furring strips and away from the joists.300.4 (D) in 2005 would not allow this. But it will allow them to install nail plates in the exception.
we have moved on to new construction.Originally posted by romeo:
This is a rough inspection on a new home,everything is open. The wires are laying on top of the furring without any staples etc. in lengths of up to 25ft. without securing. The electrician considers the cables secured because they are laying on the furring that is 16" apart. the distance from the edge of the cable ( romex ) to the bottom of the furring is less than 3/4". the question is securing of the cable because Massachusetts changed the 1 1/4"requirement to 1 1/4" Thanks romeo
That's odd.Originally posted by allenwayne:
IMO if the nm is laying on top of the furring there are no provisions that require it to be secured as it is supported.
334.30 Securing and Supporting.
Nonmetallic-sheathed cable shall be secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable at intervals not exceeding 1.4 m (41/2 ft) and within 300 mm (12 in.) of every cabinet, box, or fitting. Flat cables shall not be stapled on edge.
Sounds like a threat.Originally posted by bassphisher:
If I were in their shoes I would exactly what the inspector asked(within reason)to be on his good side.
Paul
City of Gretna Electrical Inspector
I don't see that in the Mass amendments John.Originally posted by j_erickson:
The situation which romeo describes is a violation as others have mentioned since the nm cable is not secured at proper intervals. The "laying" on top of the furring is not necessarily a violation in MA, only if it is not secured. There is a formal interpretation regarding nm cables installed "diagonal" under joists and above furring which basically says that it is legal as long as the nm cable is at least 3/4" from furring where furring intersects joist.
Romeo, what town are you in?
Not in this case Fred, in this section under discussion the firring strips are the ones used to support drywall.Originally posted by Fred S.:
From a builder's standpoint those furring strips are not the ones the NEC refers to. The NEC is refering to furring strips intended to protect wires below an unfinished ceiling, or on top of a ceiling joist in an unfinished attic.