If we can put a 60 amp breaker on #6/2 romex can we hook it to a electric furnace that has a fla of 58 amps at 220v and if not why?
Try 334.112 (2008) It is permissible if all terminations are rated for 75C
I don't have 2008 did they remove the 334.80 restriction????
Yeah right, That is the most outrageously ignored rule ever. How many people do you think run UF cable as their homeruns to outdoor panels of to a/c discos. I have never seen it. I am not arguing with you but I think there is an unwritten rule here that permits that install. Once you leave the breaker box/ disco then it is enforced around here.Keep in mind that Type NM cable is not permitted to be used in an outside enclosure.![]()
If we can put a 60 amp breaker on #6/2 romex can we hook it to a electric furnace that has a fla of 58 amps at 220v and if not why?
Keep in mind that Type NM cable is not permitted to be used in an outside enclosure.![]()
Scooby says no to the "romrex"!
"Ruh-roh!"Scooby says no to the "romrex"!
Keep in mind that Type NM cable is not permitted to be used in an outside enclosure.![]()
If we can put a 60 amp breaker on #6/2 romex can we hook it to a electric furnace that has a fla of 58 amps at 220v and if not why?
I'm curious where it says you can't use NM in a outside enclosure?
Art. 300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.8(C).
I'd say you can't use #6 anything to connect a 58A heater. Space heating is a continuous load, so the ampacity required for a branch circuit is 58*1.25 = 72.5 amps. For copper, you're looking at #4 75C conductors, or #3 60C conductors.