tonyou812
Senior Member
- Location
- North New Jersey
My buddy failed an instection last week because he had to get a circut up two floors on the outside of a house and he did it in romex. But he peeled off the outer sheathing on the romex so he wouldnt be putting" romex "outdoors (although its in pvc). but he still failed because the instpector thinks he is wrong by puting in outside where it is subject to "excessive moisture or dampness" 334.12 b. 4. Even though it was essentialy turned into thhn when it was stripped of its outer jacket. And thhn is good for damp locations as per 310.13 who is right ? If my friend is wrong than what about all the exterior lights out there wired in romex. Are they too wrong?