Maximum allowedAre you asking minimum or maximum?
I don't believe I've seen a maximum just a minimum. NEC 2017 shows a minimum of 1/4" beyond clamp for NM and 1/2" for UF.Maximum allowed
I got into a ‘discussion’ with a newly licensed electrician and mentioned the 1/4 (that’s what is was taught). He puts in in stripped wire in a box and does it later. I said it’s almost impossible to only have 1/4 of sheathing in the box. And he didn’t think I needed to be 1/4. I couldn’t remember where is was or if had been removed. Thanks!Now if you want the Code rule, its section 314.17 B 2.
A code rule is a section...this rule has been in the NEC a long time, I started wiring in 1978.
Lic electrician.... then he goes back a cuts them all inUnstripped cable in a box? Sounds like what a DIYer would do.
The only reason I can remember is I answer questions on the forum, making me look up the rules. You are welcome and thanks for using the forumI got into a ‘discussion’ with a newly licensed electrician and mentioned the 1/4 (that’s what is was taught). He puts in in stripped wire in a box and does it later. I said it’s almost impossible to only have 1/4 of sheathing in the box. And he didn’t think I needed to be 1/4. I couldn’t remember where is was or if had been removed. Thanks!
Unstripped cable in a box? Sounds like what a DIYer would do.
My 2017 shows that wording highlighted meaning that it is new for the 2017. Prior to the 2017 there was no 1/4" minimum rule if there was a connector or clamp in the box. There was a 1/4" rule when there was no clamp in the box and the NM was stapled within 8" of the box which you might be thinking of.Now if you want the Code rule, its section 314.17 B 2.
A code rule is a section...this rule has been in the NEC a long time for me its back to 1978
My 1975 codebook makes no mention of the 1/4" but does reference the 8" I mentioned in post #13.Um... the 1/4" requirement first appears in the 1975 NEC, 370-7(c).
1975 NEC:
If nonmetallic-sheathed cable is used, the cable assembly shall enter the box through a knockout opening. Clamping of individual conductors or cables to the box shall not be required where supported within 8 inches of the box.
I like those but I strip before putting cable in. Otherwise these may be easier to reach in. I never liked the 90 deg and don't use it but its available.It's not difficult with an NM-cable stripper like this one; they work decently on UF, too:
View attachment 2555778
My 1975 codebook makes no mention of the 1/4" but does reference the 8" I mentioned in post #13.
Prior to the 2017 code the rule only applied to cables entering a non-metallic box. The change in 2017 added that requirement to metallic boxes.Um... the 1/4" requirement first appears in the 1975 NEC, 370-7(c).
The NEC does not presently provide a minimum cable sheath requirement for the metal boxes with cable clamps, as is addressed in 314.17(C) for nonmetallic boxes. This wording will provide a comparable requirement and assure that the cable clamp will not bear on unprotected conductors.