Romex sheathing in a box

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The rule for leaving a 1/4" of sheathing on the cable on the inside of the box probably stemmed from those who always cut too much sheathing off.

To me the exact measurement of at least 1/4" of sheathing on the inside of the box is not really critical as long as there is at least some.
I agree, the 1/4" was never required for these until now.

952_1.jpg

Since the clamp is on the outside the 1/4" past the connector is unnecessary and most likely unsubstantiated when it was approved as a code change.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I agree, the 1/4" was never required for these until now.

952_1.jpg

Since the clamp is on the outside the 1/4" past the connector is unnecessary and most likely unsubstantiated when it was approved as a code change.
I still make sure the sheath extends past the sharp edge.
 