Romex Splicing in wall

Status
Not open for further replies.
Tyco makes a splice kit for #14 and #12 Romex. I read their brochure. It references code article 334-40.
I'm not sure if this can be used in a wall where it will be buried? Or do it still need to be Accessible?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It is being installed for new wiring, the splice kit must remain exposed after installation. If you are using it for a repair, it can be concealed after installation. 334.40(B).
 