someone told me that a person can't put two romex (one on top of the other) under the same staple. I know that the code talks about being stapled on edge but, does anybody know if it says anything about on top of each other?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

The NEC does not prohibit multiple NM cables installed under a single staple.

Many times the staple manufacture will specify how many cables should be installed under the staple.

Chris
 

rcarroll

Senior Member
Welcome to the forum.:)

The NEC does not prohibit multiple NM cables installed under a single staple.

Many times the staple manufacture will specify how many cables should be installed under the staple.

Chris
Yeah, & I hear some inspectors (not me) won't pass a job unless they have the listing. :roll:
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Yeah, & I hear some inspectors (not me) won't pass a job unless they have the listing. :roll:

I have heard that too.

Its tough for an inspector to require listed staples when the NEC doesn't require NM cable securing means to be listed.

Chris
 
Last edited:

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
I have been in the trade for over 25 years and have never seen a listed Romex (NM) staple. Since they are not listed why do we have to follow the manufactures recommendations on the box? What?s to stop me from buying barrels of staples from one of the staple manufactures and re-boxing them under my own brand name? I could put suitable for (3)14-2 or (3)12-2 NM cables.
 

whillis

Member
Location
Vancouver, BC
Iberville CIS-1 (good for 1 14/2 or 12/2 romex) or CIS-2 (good for two romex) are listed and stamped with the UL symbol. If I wasn't so lazy I'd get one from my stock and scan it :D
 

macmikeman

Senior Member
There are places where only 1 wire per drilled hole, only 6 outlets on any general purpose circuit, wire has to have the printed info facing outward, other endless variations. Thank God I live in a cool place. Not too much of that tripe here.
 

radiopet

Senior Member
Location
Spotsylvania, VA
Staples are indeed listed....check out just one manufacturer:

http://www.brisconelectric.com/STAPLES.htm

As for 110.3(B) is clearly says listed or labeled and most all staple manufactures give instructions on the box or packaging. They fall under the definition of equipment:

Equipment. A general term, including material, fittings,
devices, appliances, luminaires, apparatus, machinery, and
the like used as a part of, or in connection with, an electrical
installation.

And 110.3(B) makes reference to :

(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.

Their is a right way and wrong way to install a staple.....

Most inspectors are not going to harp on this if it looks like the cable is not damaged but if they so choose.....I believe they have that choice.
 

slick 50

Senior Member
I have been known to run 4, 5, or even 6 under a range cable staple. The NEC contadicts itself when they limit the wires under 1 staple and the area along the stud that the wires are permitted to be run. When you are running 10 wires out of a 4 gang switch box, you need realstate and it also looks alot neater with range cable staples I think...
 

Hendrix

Senior Member
Location
New England
I have been known to run 4, 5, or even 6 under a range cable staple. The NEC contadicts itself when they limit the wires under 1 staple and the area along the stud that the wires are permitted to be run. When you are running 10 wires out of a 4 gang switch box, you need realstate and it also looks alot neater with range cable staples I think...
What's wrong with cable stackers ?
 

480sparky

Senior Member
Location
Iowegia
It's just one more thing you need and one more thing to run out of. The electrical field requires sooooooo many different this and thats, you would have to drive around a school bus with a ladder rack....:grin:

Jeez, what all do you haul into a dwelling when you rough it in? Ladders, drill & cord, along with your tool pouch would be half it. Rolls of 14, 12, etc. boxes n such. would be another 45%. Wire nuts and staples will go in your pouch.

I don't think I use more than 6 or 8 on any given dwelling..... so I stick that many in my pouch. If I need more, I just grab them at the end of the day when I start taking tools out to the truck, and install them once I go back in to grab the NM that's left over.
 