electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
- Occupation
- Electrician
If disconnect is mounted on exterior a sleeve will be required since nm is not permitted in damp or wet locations per 334.12(A)(4). Also not permitted to be embedded in masonry 334.12(2). Exterior enclosures will have 1/4” gap per 404.4 and to comply with 312.2. So without a sleeve your nm will be in a damp or wet location.
Running a cable through a drilled hole is not "embedded in masonry."
The area at the back of the disconnect and around the building penetration should be sealed with silicone or similar so I do not see that as wet or damp.