- Location
- Massachusetts
Then you really shouldn't tell them about all the concrete and steel buildings that are wired 100% with NM cable here either. :lol:
You mean residential wire.
Then you really shouldn't tell them about all the concrete and steel buildings that are wired 100% with NM cable here either. :lol:
Have to run circuit from a panel to an outlet.
Run raceway out of the panel maybe 20' or 30' up and out of an electrical room into a suspended ceiling, NM or MC from there how ever far it is and then back into raceway to come down out of the ceiling with EMT into the outlet.
I find it very odd so many seem baffled by a common practice at least in my area.
You mean residential wire.
Ok well that makes sense and I also have frequently done that. I thought you were talking about a complete raceway system.
A raceway coming from a panel to a termination fitting is a "complete raceway system".
Have to run circuit from a panel to an outlet.
Run raceway out of the panel maybe 20' or 30' up and out of an electrical room into a suspended ceiling, NM or MC from there how ever far it is and then back into raceway to come down out of the ceiling with EMT into the outlet.
I find it very odd so many seem baffled by a common practice at least in my area.
So using NM the whole way eliminates a j-box or two, or is there some other advantage?
No j-box, no splices, one kind of wire to bring in etc.
Is there some disadvantage?
So they allow you to run it in a wet location which is a violation of the NEC but they don't let you run it in a conduit in a dry location which is legal. Are you sure they have a formal amendment prohibiting it?Here in San Diego's local municipalities, it's always been a no-no. We are allowed to run it in PVC conduit when going between a residence and an out-building though.
As Iwire stated no, but it is limited to 60 deg.Wouldn't you have to de-rate the due to less cooling efficiency of Romex in EMT conduit?
Nothing wrong with that code wise.He also made wire nut splices in the panel because he cut the Romex too short. (Real professional).:lol:
358.22 Number of Conductors.
The number of conductors
shall not exceed that permitted by the percentage fill
specified in Table 1, Chapter 9.
Cables shall be permitted to be installed where such use
is not prohibited by the respective cable articles. The number
of cables shall not exceed the allowable percentage fill
specified in Table 1, Chapter 9.