You can use 90deg for derating and when 90deg terminations are required but in the end you have to protect it as a 60deg conductor
(see 334.80)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I should have explained myself better (story of my life).. I was thinking about items that require 90deg rated conductors such as some light fixtures
 