NEC 230.24 covers the service drop. 230.26 covers the point of attachment. This is an instance of overlapping jurisdiction.
Under some instances NECS allows lower clearances than NEC because NESC *** -umes that utility linemen and engineers have more skill and experience sagging a line correctly than building electricians.
If there is a clearance problem, why don't you install a beside-the-building pole? Quite a few 1 story commercial buildings around here have these. If you run jacketed service entrance cable on a messenger wire from this pole to the meter socket you can get around the clearance problem. I have even seen a residential service ( in Pittsburgh, PA ) in a well to do neighborhood where SEU cable was used as the service drop and ran unbroken from the pole across the street to the meter socket.
Services are not supposed to be attached directly to a manufactured building anyways. SquareD makes an excellent meter main that is great for construction services, mobile home services, and so forth. The catalog number is QC816F200CH which has a 200 amp main breaker 22,000 AIC, 200 amp power takeoff lugs, horn bypass for the socket, and an 8 slot panelboard. If you stick in a QCGK3 generator interlock kit and backfed breaker it is also a listed manual transfer switch.