Just looking for opinions..... of course backed up with Code
Installation:
Roof top unit
Minimum circuit ampacity (per nameplate) 64
Maximum OCPD - 70
4awg copper conductors
100 amp breaker at panel
100 amp fusible disconnect at RTU fused at 70 amps
Is there a problem with the 4awg conductors being fed from the 100 amp breaker at the panel?
Thanks, Pete