An HVAC friend of mine, who is doing an "Eye Clinic", is running into trouble withe the electricians.
First off, they did not figure heat pumps into their load calculations, said that it would be an extra charge to the HVAC contractor to accommodate them. They are now complaining that they have no terminal blocks to terminate their wires for the roof top package units.
They are also saying that the duct work (which the inspector passed) was not done according to code.
I am an master electrician, have ran an electrical shop with up to 60 employees, have my own electrical contracting license / business.
I feel that the electricians under bid the job, even though there have been many electrical changes/extras that could have made up for their bidding problem.
The roof top units have wires to connect to for the back-up heat strips & the blower motor. The electricians just want to mount a disconnect to the unit & run one set of wires to terminal blocks. They argue that wire nuts should not be used to connect their wires to the wires inside the unit.
Is there such a fuse block that takes a set of 3 wires to feed it & the fuse block with 2 different sizes of fuses (3 for the heat & 3 for the motor)?
The HVAC friend had just called me about this, & it is past this old timer's bed time. Thanks
First off, they did not figure heat pumps into their load calculations, said that it would be an extra charge to the HVAC contractor to accommodate them. They are now complaining that they have no terminal blocks to terminate their wires for the roof top package units.
They are also saying that the duct work (which the inspector passed) was not done according to code.
I am an master electrician, have ran an electrical shop with up to 60 employees, have my own electrical contracting license / business.
I feel that the electricians under bid the job, even though there have been many electrical changes/extras that could have made up for their bidding problem.
The roof top units have wires to connect to for the back-up heat strips & the blower motor. The electricians just want to mount a disconnect to the unit & run one set of wires to terminal blocks. They argue that wire nuts should not be used to connect their wires to the wires inside the unit.
Is there such a fuse block that takes a set of 3 wires to feed it & the fuse block with 2 different sizes of fuses (3 for the heat & 3 for the motor)?
The HVAC friend had just called me about this, & it is past this old timer's bed time. Thanks