We have a job were the Rooftop units came with the GFCI's factory installed on the inside of the units. Since they are on the inside, can they still be considered the service receptacle?
One important factor is that the receptacle should remain energized when the local disconnect for the equipment is open.
If you disconnect the equipment for maintenance using a remote breaker, it is hard to see how the internal receptacle would get its lower.