What size single phase service is existing to the building, what size is the transformer feeding your building?
That's all ? Well, you'd still have to change the shop service disconnect and add a 3-phase panel, but that'll be a whole heap better (and cheaper in the long run) than fighting with things.We were given a price a few years ago of a bit over $30K.
That's just it, how often is it needed. How often might you need 480 volts instead of 208-240? Going to need a transformer if you need both high and low volts, or a generator that can be reconfigured for either voltage.That's all ? Well, you'd still have to change the shop service disconnect and add a 3-phase panel, but that'll be a whole heap better (and cheaper in the long run) than fighting with things.
Or rent a generator for probably $6-700/week with delivery/pickup/fuel/connection-cables... if you only need that twice a year- Maybe, otherwise it's a silly way to do things.
240 Volt single phase. Not sure of the transformer "size", but we have a 300A service to the building. It is split 150A in the office, and 150A in the shop. The place used to be a cabinet shop. When we bought the lace, we were building on boiler sets, heat exchangers, and pump sets. Today, we have gotten into doing Heat Pump/Cooling and Low Temp Cooling with refrigeration condensers for the latter. We have our own trademarked dual pass DX heat exchanger for these. The 150A in the shop is also a problem when trying to operate some of the larger equipment with other things being "lit up". In the past few days, I have finally convinced the "ownership" that a service upgrade is in order. We have since consulted with the utility, and I am getting quotes from contractors. I have also somewhat convinced them of having a propane generator with 100A capacity, with voltage selections of 120, 208, 230, 240, 460, and even to 575. (we do some overseas things now and have a certification standard with Canada and Mexico). Another part of the decision is now to maybe get the utility upgrade and a three phase variac To go with the digital converters, or a single to three phase variac, which costs a bit more, but less than the two former items commbined. . I got some help from the Mfr. Tech Rep on that one. The condenser mfr. told them they have the variacs because of UL testing requirements. Since we could be heading there, might be time to get set up. Crossing my fingers that "sense" prevails.What size single phase service is existing to the building, what size is the transformer feeding your building?
Yep. See my reply to MTW. The last line of the reply. That is what I am fighting. (And I sometimes don't know why I bother )That's all ? Well, you'd still have to change the shop service disconnect and add a 3-phase panel, but that'll be a whole heap better (and cheaper in the long run) than fighting with things.
Or rent a generator for probably $6-700/week with delivery/pickup/fuel/connection-cables... if you only need that twice a year- Maybe, otherwise it's a silly way to do things.
VFD's are good for driving motors only, and when more than one motor they all need to start/stop at same time. They especially don't like having switches/contactors on load side and adding/removing loads to an active output.Can a VFD be used to cover those voltages and both 50 and 60 Hz?
I was thinking about for Bert's testing setup.VFD's are good for driving motors only, and when more than one motor they all need to start/stop at same time. They especially don't like having switches/contactors on load side and adding/removing loads to an active output.
But isn't he driving multimotor and combination loads? That is part of why I mentioned it.I was thinking about for Bert's testing setup.
I have no idea.But isn't he driving multimotor and combination loads?
From bits of information I have seen, he may have some instances where he maybe only powering an individual compressor, but possibly has cases where powering multi - load pieces of equipment, and the controls for them. Sounds like all this is in the shop testing , not sure if for new units or for testing after repairs, how useful might depend on the reason for testing. Might be able to rig it up so that you only drive say a three phase compressor with the VFD and power anything else from the single phase source, which may be handy if they are repairing units. In those cases you might even bypass phase monitors if you had to. If performance testing new or even fully refurbished units might be more desirable to have an actual three phase supply?I have no idea.
So for practical purposes, if you need to rapidly start the motor in response to control input you must keep te rotary converter running constantly, with associated energy losses.Lastly, I forgot to mention earlier when I told you to use a standard 240V RPC or Phase perfect and put the step up transformer on the output, the transformer needs to be disconnected until the RPC or Phase Perfect gets up, running and stabilized, before you bring on the transformer and then the load.