Jimland58
Member
- Location
- Prairieville, LA
Thanks for everyone's input. As it always seems when it comes to electrical standards and regs, there is never a clear answer. The test probes we have are on a Fluke Model 115 meter which have the finger guards and have the probe caps that need to be taken off in order to fit into the receptacle blade slots. When I look at NFPA 70E, Table 130.7(C)(15)(A)(a) - Arc Flash Hazard Identification for Alternating Current and Direct Current Systems, under the task of "For AC Systems: Work on energized electrical conductors and circuit parts, including voltage testing" it says Arc Flash PPE is required. Then if you go to NFPA 70E, Table 130.7(C)(15)(A)(b) - Arc Flash Hazard PPE Categories for AC systems, under other equipment for < 240v it seems to indicate Arc Flash PPE Category 1 which means wearing rubber gloves AND ARC rated clothing of 4 cal ....... way overboard, doesn't make sense. I understand everyone has an opinion one way or the other but my question was are there any specific OSHA or NFPA requirements that an OSHA inspector could cite you if you were not wearing rubber gloves when testing voltage on receptacles?