Some research on those documents...conclussions
Some research on those documents...conclussions
Hi bphgravity,
I looked into the referenced documents; NFPA 77 does not seem to have any information on this matter, at least not in the particular subject of personal (ground) protection from shock or electrocution. NEC has two articles about insulating matting, these are 250.174(C), 640.45:
Articles transcribed from NFPA 70 2005 (NEC 2005). Published by National Fire Protection Association.
250.174 (C) On Live-Front Switchboards. Instruments, meters, and relays (whether operated from current and potential transformers or connected directly in the circuit) on switchboards having exposed live parts on the front of panels shall not have their cases grounded. Mats of insulating rubber or other suitable floor insulation shall be provided for the operator where the voltage to ground exceeds 150.
430.233 Guards for Attendants. Where live parts of motors or controllers operating at over 150 volts to ground are guarded against accidental contact only by location as specified in 430.232, and where adjustment or other attendance may be necessary during the operation of the apparatus, suitable insulating mats or platforms shall be provided so that the attendant cannot readily touch live parts unless standing on the mats or platforms.
The 430.233 has to do with protection of wiring, it says something like: so as not to present a tripping hazard they should be covered with a non conductive mat (different than an insulating mat).
NFPA 70E has three articles where matting is mentioned: Article 250, where they are mentioned as electrical safety equipment and having to be maintained in a safe work condition. Article 420.10 Guards for Attendants, identical to NEC 430.233. Annex L, Typical Application of Safeguards in the Cell Line Working Zone.
It seems there is not much official information or standards about this matter, let me give my personal point on this matter after some research done in the past days, please tell me know if I am right, wrong, any suggestions, commentaries?thanks.
As far as I can see from common sense and electrical safety knowledge, insulating matting should be used to prevent electric shock or electrocution from grounding by workers in contact with energized equipment. Therefore, matting should be placed in front of all electrical equipment operating at over 50 volts, where workers may be in contact with a live part or exposed energized equipment. In closed facilities (under roof) those could be permanent mats and outside (open air) facilities or equipment we could use removable matting.
I mentioned 50 volts instead of 150 V as NEC says, because at 50 volts you start getting some current that could be hazardous for a person. Anyway in an industrial facility we have higher voltages, but I think it should be well noted.