lj
Member
- Location
- Tampa, FL, USA
NEC 322(D) says that wiring in air-handling areas beneath raised floors for information technology equipment shall be permitted in accordance with Article 645. NEC 645 requires a means to disconnect power to all electronic equipment in the information technology equipment room. So, if all the underfloor wiring is in conduit (EMT or LFMT), is there anything else that says we must comply with NEC 645? We are trying to get away from having a disconnecting means. Thank you.[/quote]