Measuring Harmonics
Measuring Harmonics
There is difference between the real harmonic pollution and the measured one. The standard requires measurement according to IEC 61000-4-30, which is up to 49th harmony. This means that if you create pollution in frequency higher than 5 kHz (50Hz) or 6kHz (60Hz), the harmonic meter will not see all the pollution.
I had a customer which suffered from unexplained failures. He used Nexus 1252 meter which can measure up to 255 harmonics and everything was OK. I have used Elspec G4430 to measure the same site, which measures up to 5122 harmonies, and found harmonic pollution at 333rd and 334th harmonics. It was 60Hz network, which means he had pollution at 20kHz. Surprisingly, the switching frequency of his inverters was 10kHz. When he changed the frequency - the problems were solved.
Measuring Harmonics
There is difference between the real harmonic pollution and the measured one. The standard requires measurement according to IEC 61000-4-30, which is up to 49th harmony. This means that if you create pollution in frequency higher than 5 kHz (50Hz) or 6kHz (60Hz), the harmonic meter will not see all the pollution.
I had a customer which suffered from unexplained failures. He used Nexus 1252 meter which can measure up to 255 harmonics and everything was OK. I have used Elspec G4430 to measure the same site, which measures up to 5122 harmonies, and found harmonic pollution at 333rd and 334th harmonics. It was 60Hz network, which means he had pollution at 20kHz. Surprisingly, the switching frequency of his inverters was 10kHz. When he changed the frequency - the problems were solved.