You will need a through penetration firestop system, and you will not need the sleeve. You can have a sleeve if you want one, but you do not need one.
A through penetration firestop system is a spec sheet from a firestopping manufacturer that shows exactly what kind of cable is going through what kind of wall that is very specific to the particular installation. Each manufacturer has a selector on their website that shows how to do this. Example here:
https://www.3m.com.hk/3M/en_HK/faci...es/firestop-system-selector-submittal-wizard/
Probably a system like this attached pdf is what you are looking for.
Firestopping is much more complex than buying 4 hr rated caulk and slinging red stuff around whatever hole you want to fill until the inspector goes away. I can give you a lot of info and resources on how to correctly go about it if you DM me.