running 480v machine on 380v

And that was the was the initial problem:

"A step up transformer with this ratio is not avaivlbe in the market"

Unless he is in a very strange market, that constraint is an error.

Very likely the _exact_ transformer ratio is not available locally off the shelf, but with input from this crew we can probably figure out something that is close enough that the OP can reasonably get.

Any value 26% to 50% boost will do.

To @Emad : what transformers can you get? Can you get 240 to 120V single phase units? What about 380 to 120V?

Jonathan
 
And that was the was the initial problem:

"A step up transformer with this ratio is not avaivlbe in the market"
Very simple, not complicated at all.
If a transformer is not an option, there is nothing that can be done except purchasing the correct unit.

The customer may not like the choice, but the laws of physics don't offer us any choice.
 
Very simple, not complicated at all.
If a transformer is not an option, there is nothing that can be done except purchasing the correct unit.

The customer may not like the choice, but the laws of physics don't offer us any choice.
But that's point - if it was that easy a simple transformer would the job. It doesn't.
 
Many thanks for everybody for the engagement.
Now I decided to use a generator by changing its excitation and control protection to work for 480v
Will this have any impact on the generator insulation withstand? Any concerns to consider for this transformation?


Sent from my iPhone using Tapatalk

480V is a common generator voltage. If the generator is designed for 480V then there are no issues with this approach.

Does the generator have a 12 lead alternator? Different voltages are usually a combination of excitation change and alternator connection. In the systems I've worked with, excitation could adjust the coil voltage from 120V to 140V, then the coils would be connected differently to get 208V, 240V, 416V or 480V.

I would be concerned about the components outside of the alternator if they are not specifically designed for the higher voltage.

D
 
If it was that simple he would find one.
I'm not convinced he looked at all the options. He has an induction heat treatment machine and he has a 3 phase generator configurable to 480 volts. There is a transformer option that will work. It's just a hurdle, not an impossible task.

But what was your point about the output frequency of the machine? I didn't understand where you were going with that.
 
But that's point - if it was that easy a simple transformer would the job. It doesn't.
It was a simple problem. What he has for equipment does not work with what he has for a source.
If he keeps his source he needs a transformer, even if he doesnt want one, or a different model equipment.

He solution is to change his source. This is now a different discussion.
 
I'm not convinced he looked at all the options. He has an induction heat treatment machine and he has a 3 phase generator configurable to 480 volts. There is a transformer option that will work. It's just a hurdle, not an impossible task.

But what was your point about the output frequency of the machine? I didn't understand where you were going with that.
That's your opinion.
 
It was a simple problem. What he has for equipment does not work with what he has for a source.
If he keeps his source he needs a transformer, even if he doesnt want one, or a different model equipment.

He solution is to change his source. This is now a different discussion.
I don't believe so. That's because it now a different problem.
 
Completely off topic but since we have someone from Lybia so rarely
@Emad do you still commonly use type L receptacles in Lybia?
Are the nominal voltages still 220Y/127 and 380Y/220 ?
Or have they moved to 230Y/400?

Yes@tortuga
We are now using type L outlets and power system is 380/220v 50hz.
However,there are a little number of old Oil fields that they still use 220y110 ,whose I believe established by Amharic companies in early 1960s


Sent from my iPhone using Tapatalk
 