Running a ground without pulling out the feeder conductors

Status
Not open for further replies.
rcwilson said:
What is a safer installation - 3 phase 4 wire with no EGC, or 3 phase 4 wire with an EGC run nearby in a PVC conduit? The impedance of the temporary EGC in a seperate conduit is more than an EGC run in the same conduit as the phase wires, but it is probably still less than the exisitng ground path.

I am not recommending going against a code requirement. I am just pointing out an application of Ohms law.
Bob,
But a permitted "rebond" of the neutral at the second "structure" would be an even lower impedance fault clearing path than an EGC in the same raceway as the feeder conductors.
 