Orenco makes small sewage lift pump panels, for what's called a "force main" system where a lot of small individual pump stations at each house (or maybe pair of houses) collectively feed into a pressurized sewer main to force the flow up hill toward a treatment plant, rather than have to use gravity feed down into bigger lift stations. I did a project about 25 years ago with 123 Oronco panels in a housing tract around a lake, all of them "rated" for 240V single phase, all of them fed with 208V. No issues whatsoever. The sewage pumps on my project were all 3HP or less and rated for 208/240V single phase. The FLA at 208V was a little higher, but these submersible pumps were self protected and only ran for a few minutes at a time at worst. So I didn't even have OL relays that had to be adjusted.
The more important people to check with though are the pump suppliers, the Orenco panels themselves couldn't care less. The controls and electronic power supplies are all tapped off of 120V taken from Line to Neutral, and that will be the same no matter what. The 208 or 240V is just passed through to the pumps.