saghalib
We have a Metal Enclosure in a chemical plant that is installed outside in open. The Enclosure has some AC to DC power supplies and some DC equipment installed on a metallic back plate. In order to feed the power supply there is a 3 wire 220 VAC power entering the FEC. The green equipment ground conductor with this cable goes to a Grounding Bus Bar (which has insulated footing so it does not touch the enclosure or its back plate). From this bus bar the ground cables go to the AC to DC power supplies.
Apparently there is an another Grounding cable connected to the enclosure body from outside of enclosure. This is basically is a single conductor connecting to all metal poles, enclosures and structures around and also connecting to electrodes driven into EARTH after regular intervals. What I am not sure about is that if this Main ground cable is going back to the power source or not, but some of the inspectors are calling it Plant Grid.
Now what I want to do is to connect the equipment grounding conductor that is entering along with 220 VAC hot and neutral wire into the enclosure , to the enclosure body as well. My understanding is that the Grounding bus bar that has connection to this grounding cable as well as to power supply ground terminals, also needs to have bonding jumper connected to the enclosure body. But the inspectors are saying that you should not connect this equipment ground conductor to the enclosure body since Enclosure body is already grounded using that main grounding system (the plant grid).
Should I still connect to the enclosure and have multiple grounding conductors going back to the source? Only one conductor is enough? if one then which one is better option?
What exactly is this Plant Grid? if these are the ground conductors connecting to metal enclosures and then going back to the source then why do I need to even have 3rd equipment ground cable with main power cable then?