petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
Your 500's are also undersized for a 2000 amp feeder. 380 amps * 5 = 1900 amps.
lets pile on.
Your 500's are also undersized for a 2000 amp feeder. 380 amps * 5 = 1900 amps.
What is this a feeder, SEC's, transformer secondary conductors?
You called it out as rigid conduit. If it is rigid steel conduit, no egc of the wire type is even required, at least in general.
Main service conductors that are feed from load side of 13800/480 step down.
No, the 1/0 limit does not apply to equipment grounding conductors.
Im not too worked about this, but yes it is enough because all of this is below grade and ambeint temp derates say its ok. Thats another story though. Thanks for the help.lets pile on.
No equipment grounding conductor is required to be run with service conductors. A main bonding jumper would be installed at the service disconnect enclosure to bond the enclosure, grounded conductor and equipment grounding conductors. A ground electrode conductor will also be needed to connect the enclosure, grounded conductor and equipment grounding conductors to the grounding electrode(s).
So, are you suggesting that since the parallel rule does not apply to EGC's, that it is ok to take #3 AWG into 5 separate pipes to create and essentially equivelant 250KCMIL at the gear?
No. I'm suggesting that for a 2000A feeder with 5 parallel sets, if using conductor type EGCs, you would need 5 250mcm egc's, one in each conduit.
I'm also suggesting that for a 600A feeder with 2 parallel sets, you could use 2 #1awg (smaller than #1/0) egc's, one in each conduit.
In both of David's examples you're not running smaller EGC's to make a larger one you're running a full size EGC in each raceway.
Supply-side bonding jumpers between a transformer secondary and the secondary conductors OCPD can be sized according to the conductors within each raceway.
In both of David's examples you're not running smaller EGC's to make a larger one you're running a full size EGC in each raceway.
Supply-side bonding jumpers between a transformer secondary and the secondary conductors OCPD can be sized according to the conductors within each raceway.
I was under the impression that you only need one (1) 250KCMIL condutor in on of the pipes and just bond the rest with bond bushings from the 250KCMIL. Why would you need a 250KCMIL in each conduit with you only need to have EGC rated for the breaker size. If you run one EGC at 250KCMIL and jumper the others, you have essentially done met code. My question was based on conduit restrictions. We were trying to use 5 - #3 THHN wires (one in each conduit) to suffice the one (1) 250KCMIL required EGC?