Taking 200A service 675 feet from Meter main to sub panel. This requires 750 mcm in 2 parallel sets. Any advice on whether its easier to run both sets in one 5" PVC or use two runs of 4". Its a pretty straight shot down a hill side from the panel to the meter.
Also the calculation for 600 mcm is around 667 feet (really close), so if the load demand is less than 200A could the wire be downsized to 600 mcm?
your connected load should not exceed 80% of the service limit.
however, based on 200 amps..... assuming this is 240v 3w service?
120 to neutral is killing you. bump it up to 480, and then back down.
the wire cost for parallel 750 aluminum is far more than the transformers.
two 4/0's and a ground will get you there with 2.44% voltage drop.
it'll legally fit in a 1 1/2" conduit, but you'd be crazy to use less than 2".
a 120/240 ~ 480 dry type transformer of 75 kva will do nicely. you need 48 kva.
$1650
4,200 ft 750 mcm aluminum $10,920
700' 2" pvc
1400' 4" pvc.
you get the idea.
i've pulled 500mcm aluminum thru 4". 750mcm, you can put 3 and a 250 gnd in 3 1/2.
most folks use 5" for something like 750, which most people won't pull. they will use 500's in parallel.
pulling 6 750 mcm and two grounds in a 5" pipe comes out to 36% fill.
you'd be nuts to try that in a single pipe, in my experience.
but... were you to try it, i'd love to bring popcorn and watch....