One UL listing = one piece of equipment.
So what do you do when the manufacturer's instructions state to use two NMs?
Note please that the unit is wired with separate neutrals for the two load groups. There is no connection between them at the fan (so no parallel wiring) and each neutral carries only the return current for its load.
If you chose to tie the two white wires of the fan unit together at the fan j box it would create a violation.
You are right, it could be if you jump through all the needed hoops to do so.
And then the inspector looks at it when you are not there, makes a mistake, fails the job and things are delayed
Run the numbers on that and see if it makes sense to do so vs a 10/3.
The violation is that not all of the conductors are in the same cable.
An exception for running separate conductors in two or more non-ferrous raceways does not directly apply to cable wiring methods.
There's "code-compliant" and "something you don't mind attaching your name to".
This is an instance where I don't care if I wind up driving two hours, don't care how technically correct I am, and don't care if I am walking with the inspector to explain or not, and don't care if the inspector is sharp enough to understand that it's legal; 10-3 goes in the wall. You don't need condoning or executing something as hack as this following you around for years to come.
Except when it's 3:15 on a Friday.
talk them out of the dang night lite
The fault is on the GC not telling you what the house needed in the first place. Looks like 10/3 to get your inspection.
Looks to me like the submitter was trying to get an exception specifically for underground non metallic raceways, the CMP simply mentioned that those are already covered by current wording.Apparently, did you look at the thread I referenced? By CMP 3:
Recommendation:
Delete the following:
Exception: Conductors installed in nonmetallic raceways run underground
shall be permitted to be arranged as isolated phase installations. The raceways
shall be installed in close proximity, and the conductors shall comply with the
provisions of 300.20(B).
Substantiation:
The exception is not required. Such installations are permitted
by 300.3(B)(3) in all locations, not just underground locations.
Panel Meeting Action: Reject
Panel Statement: This exception is necessary to permit installations where
nonmetallic raceways are installed in close proximity with all of Phase A in one
raceway, all of Phase B in another raceway, all of Phase C in another, and all
the grounded conductors in another raceway. Where this is useful is between
underground manholes so the phase conductors can exit the raceways and be
easily racked within the manhole, taking up less space, and making it easier to
do testing and maintenance on the installation. This would not be permissible
without this exception.
Number Eligible to Vote: 13
raceway,....
I agree with Wayne, et. al., that a pair of 10/2 NMB cables that are an Electric Clothes Dryer 30 Amp 240 / 120 Volt branch circuit meeting the requirements of 300.20(B) IS a Code compliant installation and the inspector is wrong.
Not if you parallel the neutrals, for sure.