We're reviewing the code requirements (551.7X Recreational Vehicle Parks) and have several questions.
Looking at putting in at the RV dealer power for trailers for sales demonstrations. 551.77 (A) states that the electrical supply equipment has to be located on the road side of the trailer, no more then 5-7 feet from the side. Would this requirement apply to an RV dealer?
Our plan is to set pressure treated 6 by 6 poles in the ground and mount two separately fed 50A outlets on one pole. One pole would be shared between two trailers with the separate outlets. Alternatively we would have to install a pole behind each trailer.
With the light load (sales demo) we plan on feeding each outlet with #10 wire protected with 30A circuit breakers. The conductors will be THWN in 1" CPVC buried 18" deep (minimum).
Thoughts?
Thanks
Mark