Rv/ Mobile home park

Status
Not open for further replies.

packersbay

Member
Location
New mexico
Occupation
Electrician
I have a customer who is wanting to upgrade all the electrical on a RV/ mobile home park. Currently they have a mix of both and have pedestals on each lot. The lot is about 86 total.
The have 200amp disconnects and assuming they are daisy chain to each pedestal. Not sure how many are daisy chained together. Everything is underground to each pedestal. Customer wants 200amp service on each lot, so they can have either a mobile or RV on lot. My question is how many mobile homes can be daisy chained on a 200amp disconnect. And can I put 200amp pedestal on each lot.or do they have to be individually. I also thought of just setting a pole with 200amp service on each lot and go overhead.
 
You need to review Art 550.31 & .32. There are significant demand factors involved so you can definitely feed more than one unit olff a 200 amp service..
Considering NewMexico heat I might not want to take full advantage of the allowances :)
 