I have been reviewing Article 551 in preparation for designing an RV park electrical renovation, where all the existing service pedestals are being upgraded to 50-ampere pedestals. I am trying to understand the permissible demand factor table (Table 551.73) in light of voltage drop calculations.
551.73(C) seems to give permission to apply the demand factor to the individual load as well as the total load. Since I intend to run individual dedicated feeders from the service panel to each pedestal, I am not sure I can apply the demand factor to the feeder. Also, the fine print note warns against using the demand factors in areas of extreme temperature. Since this is south Georgia, it might not be a good idea to apply any demand factor at all.
However, if no demand factor is applied, the voltage drop to the farthest pedestals dictates use of a wire size (1/0 AWG) which will not fit under the lugs of a 50-ampere breaker.
My only alternative appears to be to provide additional distribution panels so that the distance to the load is reduced.
I am hoping someone might have some thoughts on whether it is permissible to apply the demand factors to the dedicated feeders in this case.
551.73(C) seems to give permission to apply the demand factor to the individual load as well as the total load. Since I intend to run individual dedicated feeders from the service panel to each pedestal, I am not sure I can apply the demand factor to the feeder. Also, the fine print note warns against using the demand factors in areas of extreme temperature. Since this is south Georgia, it might not be a good idea to apply any demand factor at all.
However, if no demand factor is applied, the voltage drop to the farthest pedestals dictates use of a wire size (1/0 AWG) which will not fit under the lugs of a 50-ampere breaker.
My only alternative appears to be to provide additional distribution panels so that the distance to the load is reduced.
I am hoping someone might have some thoughts on whether it is permissible to apply the demand factors to the dedicated feeders in this case.