NEC 2008 applies. Consider a single site at an RV park. The power pedestal has breakers and outlets for 20, 30, and 50 amps. 551.73(A) tells me to calculate the feeder load at not less than 9600 VA. At 240 volts, that equates to 40 amps. I would like to supply this power pedestal with a 50 amp, 120/240 volt, single phase breaker, using a wire with an ampacity of 47.5 amps.
Whatcha think? Legal? Illegal? Cheating? I?ll tell you why I am asking, after I get a few opinions.
Whatcha think? Legal? Illegal? Cheating? I?ll tell you why I am asking, after I get a few opinions.