I am looking at an RV park with 21 sites on it and need help checking my calcs. The customer wants all sites to have 50a 250/125v at each site. I come up with 378a of load. Utility will be single phase 120/240 sevice. Can I get away with installing a 400a service? The temprature here is usually temperate enough to never need Air conditioning. Maybe just a small space heater. Most of the sites will be occupied by trailers not big Diesel pushers. If the cust. ever wanted to expand to other sites it would be near impossible with voltage drop taken into consideration. It would be cheaper to have the POCO drop a new service down the road, to save on the super sized conductors. I am just a bit fuzzy on loading a 400a service to near its maximum capacity (not that it will ever happen). This is really one of those jobs I feel that looks worse on paper than it actually will be.
21 sites x 9600va = 201,600va
201,600va x 45% demand factor = 90,720
90,720va / 240v = 378a
Any help or suggestions would be greatly appreciated.
21 sites x 9600va = 201,600va
201,600va x 45% demand factor = 90,720
90,720va / 240v = 378a
Any help or suggestions would be greatly appreciated.