Hey everybody, just wondering if I to install a RV receptacle 50 amp 240 V outside. Does that have to be on a GFI breaker or can I put that on a standard to plow 50 breaker?
See 551.71(F) TIASee 210.8(A) & 210.8(B)
Who legally responsible? If something was to happen.Put in one last month, called the inspector to find what code cycle they were on, he said they were requiring gfi, but due to shortages, if I didn’t, he wouldn’t turn me down.
Do you know of any problems from lack of GFCI protection on a feeder/service for an RV before this rule was adopted?Who legally responsible? If something was to happen.
The 2020 code has a specific rule for this in 210.8(F).See 210.8(A) & 210.8(B)
If this receptacle is at a dwelling unit, the rules in 551 do not apply to the receptacle. Those in 210.8, specifically 210.8(F), do.See 551.71(F) TIA
I was able to find both a 30 amp single pole and a 50 amp two pole online, so I’m not worried about it. Had plenty of space too. The customer wanted to have future EV and solar connections, so I also found a meter/main 3r loadcenter that was solar rated. Supply house here never heard of a solar rated panel.Who legally responsible? If something was to happen.
Which edition of NEC applies?Hey everybody, just wondering if I to install a RV receptacle 50 amp 240 V outside. Does that have to be on a GFI breaker or can I put that on a standard to plow 50 breaker?
Same here, I’ll have to look that upI was able to find both a 30 amp single pole and a 50 amp two pole online, so I’m not worried about it. Had plenty of space too. The customer wanted to have future EV and solar connections, so I also found a meter/main 3r loadcenter that was solar rated. Supply house here never heard of a solar rated panel.