RV receptacle
Farmfly
North Carolina
Hey everybody, just wondering if I to install a RV receptacle 50 amp 240 V outside. Does that have to be on a GFI breaker or can I put that on a standard to plow 50 breaker?
May not be quite that simple.
Depending on the location\use of this receptacle it could fall under article 551 which also has a TIA that allows it to not be GFCI protected
This might help to explain.
  • TIA Log No. 1653, HVAC GFCI, 05-27-2022.pdf
you got to look at your states Amendments. Your seems to say you still have to have that GFCI.
Dump looks like oregon going that way this year.
Can't say for any other areas, but here the inspectors are allowing us to omit the GFCI. The RVs have GFCI protection inside.
Put in one last month, called the inspector to find what code cycle they were on, he said they were requiring gfi, but due to shortages, if I didn’t, he wouldn’t turn me down.
Who legally responsible? If something was to happen.
Not saying it’s a problem, but if something does come down, who would be responsible in the situation he mentioned?
I think all this gfci is a tad overkill even if it does help.
I was able to find both a 30 amp single pole and a 50 amp two pole online, so I’m not worried about it. Had plenty of space too. The customer wanted to have future EV and solar connections, so I also found a meter/main 3r loadcenter that was solar rated. Supply house here never heard of a solar rated panel.
Which edition of NEC applies?
2017 - if at a dwelling not required. Not at a dwelling probably so.
2020 - probably required regardless of dwelling or non dwelling.
Then comes what may or may not been amended where this is at.
Same here, I’ll have to look that up
So quick look seems there ratted at 120% the typical panel rating