RVSS motor starter and branch circuit

Merry Christmas

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have an existing 460V 3phase 60hp TEFC induction motor that needs to be upgraded to 75hp. (This application is for a torque motor that controls a large gate). The motor starter is a RVSS-reduced voltage soft starter- which will probably have to be increased in size. But does the motor branch circuit need to be upsized to the locked rotor current (I.e. 6 x motor FLA)
since it’s a high torque scenario? Or does the RVSS mitigate that requirement?


Enviado desde mi iPhone utilizando Tapatalk
 
Adding 15 hp load? The entire branch circuit, OCPD and any disconnects upsized absolutely. 75 hp = 96A (430.250)

RVSS does nothing to this required service.
 
I've done a lot of gate/valve operators and all of the electric ones have been gear motors. 75 HP sounds big. We did some butterfly valves for Philly Southwest wastewater treatment plant and they were big valves (combined wastewater/stormwater flow for that whole drainage area), and those were only like 20hp if that
 
That's what I'm trying to figure out. A gear reduction motor drive is not a "high torque" load. The biggest high torque loads are on massive air compressors, giant blowers, conveyor drives in mining, gravel etc. Extreme situations. I just want him to get the correct soft start for the upgraded 75 hp motor upgrade.
 