LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
One tapped feeder for me, too. Maybe even a panel if there's the possibility of any future additional loads.
I asked the same - but at 95a running - the inrush for a motor that big, both combined would be huge for say 1/0-3/0cu - then there is a voltage drop to consider.....iwire said:First I would ask if both compressors must run simultaneously, often they do not.
K8MHZ said:Also be sure to inform him that he needs to be assured that the O.D. of *any* conduit used must exceed the I.D. or else the hole will be on the outside of the pipe.
e57 said:Don't know where you guys are going.... (But if the beers good...)
And thats the question - "Would you do two runs sized for 95a @ 125% for 250' - or one run for both?" - Me still trying to sort out 'tap rules, the job I'm going to, whats 4/0 in the table? - derating would apply if in one conduit, 2 circuits'
Me - "Sorry gotta go - I would do one run as a feeder - tap in a gutter between them both to two disconnects - but you have to check the tap rules.... Gotta go..."
e57 said:Seems well qualified - I actually got his number called him later and told him to join here....
I voted other because I would have said "Why dont you call an electrician?"e57 said:I get these from time to time.... Guy you don't know asks very knowagable counter guy a question - counter guy looks at you - do you answer or what? If you answer what do you say?
Heres the question:
Got 2 HUGE compressors - both identical - 95a each according to table values - a 250' run overhead inside.
Sure, I talk to other people while at the supply counter. News, weather, sports.quogueelectric said:I voted other because I would have said "Why dont you call an electrician?"