local inspecter applies this to outside residential panels , real ugly do do what do you think?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: saction 312.5 A-C

I don't understand, what's the problem?

Roger
 

3way

Member
Re: saction 312.5 A-C

He has virtualy outlawed outdoor res. services by not alowing gang entries thru 2" KO in back, LB from under allows 1/2 /3/4 KO added in backor LB out of top
 

hurk27

Senior Member
Re: saction 312.5 A-C

Sounds like you in Cal. Are you talking about bringing your branch circuits into the panel through a 2" k/o? If so the NEC don't allow it ether. Unless it is a surface mounted panel and then it only allows for it to inter through the top. Look at 312.5(C) exception
 

tom baker

First Chief Moderator
Staff member
Re: saction 312.5 A-C

Each cable has to be secured. Running thru a LB and stubbing a nipple into a wall or crawl is a violation, with out securing the NM to the conduit.
Now 312.5 has an exception but it is limited. there are some other issues with running thru the LB such as wire fill and derating...
 

jgriffin

Member
Re: saction 312.5 A-C

local inspecter applies this to outside residential panels , real ugly do do what do you think? (REAL UGLY DO DO?),... Sounds like you're on the receiving end of a joke, OR YOUR post was a joke. I'd Confront the Inspector and ask If he has a PROBLEM with your Panels and Go from there.

[ February 24, 2004, 09:13 AM: Message edited by: jgriffin ]
 

3way

Member
Re: saction 312.5 A-C

312.5 talks about cabinets cut outboxes meter sockets does this apply to a surface 200 amp

RT service panel? or is it service equipment (definitions)?
 