You might be better off putting the lower voltage transformer over by the new loads.
You might be better off putting the lower voltage transformer over by the new loads.
Not this one ..
View attachment 2562694
I'm trying to eliminate having a 60 A 120 v panel if possible.
The neutral for a 120/240V output would be provided at the X2,X3 connection. It would need to be bonded to the EGC and connected to a GES.
I did plan on that as well, although I changed up my game plan with eliminating a closer 3 phase 277/480 source and go with the undersized 120/240 system 40' further. As noted on my drawing below.You might be better off putting the lower voltage transformer over by the new loads.
I could, although Id still need the buck boost transformers I believe, because the stepped down voltage will still drop down below a safe level after 300-400 ft. its a tough call on which scenario really is more cost effective.Why wouldn't you just connect X2 and X3 and then ground them? X2-X3 would be your neutral point.