Gar
Oops that was a mistake. I am specifically referring to a high leg delta configuration.
By safely I really mean without overloading any breakers or fuses and having enough head room so that plugging in a small appliance or stero or something of the sort doesn't trip a main breaker or fuse.
I think my question was worded poorly. I guess what I'm wondering is if it is possible to distribute 240v loads on a high leg delta configuration in such a way that the current from all three legs are balanced thus utilizing the full power capacity of the panel? Or will the current on the high leg always be less?
If you balance the line to line loads evenly across all three phases, it will result in equal currents in all three ungrounded wires.
The fact that you are looking at a high leg delta does not change that in the least.
Your problem is that if you put balanced line to line resistive loads on a wye source you can calculate the total power in two different ways:
You can multiply the load (single line to line) currents by the line to line voltage and add up the three terms.
Or you can multiply the line current (resulting from two line to line loads, out of phase) by the line to neutral voltage and add them up.
The two results must be exactly the same, since the source cannot tell whether the line currents result from a balanced delta load or a balanced wye load.
Your problem is that you are trying to make a similar calculation using the line to neutral voltages in a high leg delta. That simple current times line to neutral voltage calculation does NOT work in this case since the current in the A and C wires is NOT in phase with the A or C to N voltage.
The fact that the B leg is carrying the same current as the A and C legs but has a higher L-N voltage does NOT mean that the B leg is somehow supplying more power. If you do the calculation correctly, the sum of the three voltage x current x power factor products will be equal to the delta calculation of the simple application of the three phase power formula.
As an example of why your calculation does not work, look for a moment at a corner grounded delta with a grounded B leg.
It is not true that all of a sudden the B leg does not provide any power. And the line currents in A and C are NOT in phase with the A-B or A-C voltages.