Post 11 assumes the breaker will trip at exactly 80 amps in his calculations.Why are you saying a 100 amp breaker will trip at 80?
What am I missing?:huh:
Post 11 assumes the breaker will trip at exactly 80 amps in his calculations.Why are you saying a 100 amp breaker will trip at 80?
What am I missing?:huh:
And that is an incorrect assumption.Post 11 assumes the breaker will trip at exactly 80 amps in his calculations.
Post 11 assumes the breaker will trip at exactly 80 amps in his calculations.
Why are we assuming that? It is not reality.Assuming the breakers will trip at 80% capacity,
Which make no sense and why I asked about it in post 12.
The problem is the assumption that a breaker will trip at some arbitrary level is not theory. The theory problem I see here is that the OP is not seeing that L- L loads are all served by 240V windings and will only see 240V, not 120 or 208.Why? Because he doesn't care about reality, only the theoretical at this point.
Because he doesn't care about reality, only the theoretical at this point.
Ok, imaginary, hypothetical?The problem is the assumption that a breaker will trip at some arbitrary level is not theory. The theory problem I see here is that the OP is not seeing that L- L loads are all served by 240V windings and will only see 240V, not 120 or 208.
Roger
If your loads are 240v and the transformer supplies 240V L-L. We don't care what the L-G voltages are, nor does the load.
OP wants to consider the code or just the theory
L-L, and L-G or L-N only tell us that you have a Delta configuration. It does not tell us if it is Open or Closed Delta
Only that 80 amps = 80% of 100 amps and that his theoretical CB will magically trip @ exactly 80+ amp. No more, no less.
You also figure that as 5 kVA per line, but not at 240 per line, not at 120 per line, not at 208 on the high leg, but at 138 volts per line, that is what the mid point of the delta would be. 208 is not the midpoint, it is a measurement of the distance from one point from the opposite side of the triangle. 120 is only a mid point of one side of the triangle, but does apply for unbalanced 120 volt load calculating.
But again as OP question is asked a 100 amp three pole main breaker can be loaded to 100 amps per line, but that don't mean you are as likely to have equal current ability per line from the source as you typically have from a wye source with a high leg delta system. Open delta systems don't have equal line current ability, period. Sometimes you do run into a full delta system where they expect higher load on the 120/240 side and put in a bigger transformer for that side, but you can not load the high leg to the same capacity as the other two transformers are not large enough to do so, the 100 amp main will not know any better though.
The theory problem I see here is that the OP is not seeing that L- L loads are all served by 240V windings and will only see 240V, not 120 or 208.
Safely to who, to what standard and in what circumstances? I could safely carry 100 amps on 14 AWG under the right conditions.
That the panel is from a wild leg delta has nothing to do with the question except that the source is a delta. Actually the source could be a wye and it does not change the answer.
The answer is obviously 80*138*3 = 11040*3 = 33120 W. Note 138 is a rounded value. The exact value is closer to 138.5641 . Because of this rounding some of the values below are not as close as you might want.
Two different resistive loads will accomplish this or some combination.
But now for the second half of the question:
How would the loads be wired such that they take full advantage of the available power?
Theres 3 different L-L connections. AB, BC, and AC. C is clearly the high leg.
Now if we loaded just one of the LL connections with all 33120w I'm pretty certain the theoretical 80amp breakers would flip. We need to balance the loads across all three.
Would each connection be loaded to 33120/3 = 11040w? Or would the BC and AC be loaded slightly more and the AB slightly less since the C leg has more potential?
You can. That is the only "normal" use of the B leg, namely to feed three phase loads. 240V single phase loads can connect that way tooIf the load is 240v single phase why cant you put a breaker between A-B or C-B? (In this diagram B is the highleg) Wouldnt that use the third leg?
View attachment 17087
For strictly 240V resistive loads it makes no difference which is the wild leg, but FWIW Code requires B to be the wild leg on premises wiring. Some POCO require C to be the wild leg for metering purposes and Code permits this, but C must be flopped to B immediately thereafter....
Theres 3 different L-L connections. AB, BC, and AC. C is clearly the high leg.
For calculating total load you should use the conventional formula:Now if we loaded just one of the LL connections with all 33120w I'm pretty certain the theoretical 80amp breakers would flip. We need to balance the loads across all three.
Would each connection be loaded to 33120/3 = 11040w? Or would the BC and AC be loaded slightly more and the AB slightly less since the C leg has more potential?
80A × 240V × √3 = 33,255VA
And being purely resistive loads, that converts directly into Watts (VA × PF = W).
Loads are the same as voltage in the respect that they require two points having a voltage differential. In balancing the loads, it will be 33,255VA ÷ 3 = 11,085VA per LL pair. What you will want to note for later discussion is that 11,085VA ÷ 240V = 46.2A and 46.2A × 2 = 92.4A which is significantly more than 80A. Can you tell us why?