Woot we have an answer!! Thank you guys for staying with me.
If your loads are 240v and the transformer supplies 240V L-L. We don't care what the L-G voltages are, nor does the load.
L-G was given just to make it clear what kind of power we have
OP wants to consider the code or just the theory
Just theory
L-L, and L-G or L-N only tell us that you have a Delta configuration. It does not tell us if it is Open or Closed Delta
This would tell us what type of transformer is used correct? But if we assume the transformer has no limitations would this matter?
Only that 80 amps = 80% of 100 amps and that his theoretical CB will magically trip @ exactly 80+ amp. No more, no less.
Exactly! I suppose I choose 80 amps because it leaves room on the breaker for other things, changes in temperature, etc. If a client asked you to load as many 240V resistive loads onto a panel of this sort (100amp 3ph high leg delta w/ oversized transformer) as he could and there were also small L-N loads and power outlets and the such how much would you add? More? less? I feel like 20 amps of head room on each leg is appropriate for whatever else might get plugged in or used.
You also figure that as 5 kVA per line, but not at 240 per line, not at 120 per line, not at 208 on the high leg, but at 138 volts per line, that is what the mid point of the delta would be. 208 is not the midpoint, it is a measurement of the distance from one point from the opposite side of the triangle. 120 is only a mid point of one side of the triangle, but does apply for unbalanced 120 volt load calculating.
ahhhh I see!!
But again as OP question is asked a 100 amp three pole main breaker can be loaded to 100 amps per line, but that don't mean you are as likely to have equal current ability per line from the source as you typically have from a wye source with a high leg delta system. Open delta systems don't have equal line current ability, period. Sometimes you do run into a full delta system where they expect higher load on the 120/240 side and put in a bigger transformer for that side, but you can not load the high leg to the same capacity as the other two transformers are not large enough to do so, the 100 amp main will not know any better though.
Good to know but I really wanted to assume that the transformer doesn't present any limitations. Lets assume for example it is way over sized.
The theory problem I see here is that the OP is not seeing that L- L loads are all served by 240V windings and will only see 240V, not 120 or 208.
I understand that L-L voltages are 240, that is the reason why I made all the loads 240 and not 120 or 208.
Safely to who, to what standard and in what circumstances? I could safely carry 100 amps on 14 AWG under the right conditions.
Haha I remember reading about the guys near Switzerland that shoot little particles around a 17 mile underground tunnel at speeds close to that of light. They need insane amount of current and obviously don't have unlimited amounts of copper. I'm pretty sure they do something like that. I think liquid nitrogen is involved
That the panel is from a wild leg delta has nothing to do with the question except that the source is a delta. Actually the source could be a wye and it does not change the answer.
The answer is obviously 80*138*3 = 11040*3 = 33120 W. Note 138 is a rounded value. The exact value is closer to 138.5641 . Because of this rounding some of the values below are not as close as you might want.
Two different resistive loads will accomplish this or some combination.
Thanks gar. I see now. You use the mid point of the delta.
But now for the second half of the question:
How would the loads be wired such that they take full advantage of the available power?
Theres 3 different L-L connections. AB, BC, and AC. C is clearly the high leg.
Now if we loaded just one of the LL connections with all 33120w I'm pretty certain the theoretical 80amp breakers would flip. We need to balance the loads across all three.
Would each connection be loaded to 33120/3 = 11040w? Or would the BC and AC be loaded slightly more and the AB slightly less since the C leg has more potential?