Not only are the salesmen at the door with their safety controllers but they are darn close to selling the things to peeps here. NFPA79:2002 9.4.3 allows the use of programmable devices in a safety circuit providing it gives the same protection as hardwire. NFPA79:2007 adds additional cautions on how to handle the software.
I need some decent arguments to keep these critters out of the plant. Some of the peeps are willing to buy on the side so I need to get this headed off with safety. According to our local contract we cannot prevent our general electricians from tampering with these devices as 2007 requires.
Up to now I've answered these peeps with:
"The software is an integral component to the PLC; therefore the software has to be listed for use as a safety device just as the hardware is listed."
Similar to the edict that if you modify a UL listed device it is no longer considered UL listed.
Any additional suggestions?