Re: same bored hole, here we go again
This is not a wives tale. A conductor is not a cable. Once a conductor is inside of a cable the assembly becomes a cable assembly or as we commonly call it a cable. A cable and a conductor are not the same thing. The 2" separation required is from conductors not cables.Originally posted by websparky:
Trevor, I disagree.
This must be one of those "wifes tales".The key word is conductors not cables. There is a requirement for a 2" separation from open conductors not cables. They are permitted in the same hole.
Look up the definition of "conductor as used in the NEC. Also look at article 310.4. Here is an excerpt:As you can see, the article 800.52 referenced by david is correct. This means that NM cable does qualify.Where run in separate raceways or cables, the raceways or cables shall have the same physical characteristics. Where conductors are in separate raceways or cables, the same number of conductors shall be used in each raceway or cable.
(2) Other Applications. Communications wires and cables shall be separated at least 50 mm (2 in.) from conductors of any electric light, power, Class 1, non?power-limited fire alarm, or medium power network-powered broadband communications circuits