Same xfrmr feeding 2 diff swiches

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Scenario, same xfrmr feeding two different switches.

Building 22 switch being feed with 4 sets of #500 & 1 #1/0
Building #23 switch being feed with 5 sets of the same size wires.

To me it looks( the dot) like they are calling for either feeder to be tapped. I know you can’t run the sets for both switches from the xfrmr, meaning it can’t directly feed them so it has to be a tapped, correct? Could one one Ilsco tap blocks for this application? Seems a bit tricky. Need a big tap box as well. Thanks.
 

Attachments

  • FEEDERS 1.jpg
    FEEDERS 1.jpg
    12.2 KB · Views: 0
  • FEEDERS 2.jpg
    FEEDERS 2.jpg
    10.8 KB · Views: 0
Scenario, same xfrmr feeding two different switches.

Building 22 switch being feed with 4 sets of #500 & 1 #1/0
Building #23 switch being feed with 5 sets of the same size wires.

To me it looks( the dot) like they are calling for either feeder to be tapped. I know you can’t run the sets for both switches from the xfrmr, meaning it can’t directly feed them so it has to be a tapped, correct? Could one one Ilsco tap blocks for this application? Seems a bit tricky. Need a big tap box as well. Thanks.

I don't see why the connection cannot be made right at the transformer. Whether it is a legal tap or not is something else that IMO is not dependant on whether the connection is made at the transformer..
 
You can have multiple sets of conductors running from a transformer. Is the transformer located outside? If not, you will be limited by the 25' rule in 240.21(C)(6). If the transformer is outside the rule in 240.21(C)(4) will apply permitting unlimited conductor length as long as the installation complies with all of the rules in that subsection.
 
I don't see why the connection cannot be made right at the transformer. Whether it is a legal tap or not is something else that IMO is not dependant on whether the connection is made at the transformer..

9 sets leaving xfrmr?? Where the hell would all the conductors terminate? :dunce:
 
You could use something like this with one on each side of the spade for 16 terminals.

But still don't understand how it's possible to come out of the xfrmr with 16 sets of 4". Does not seem like there would be enough room for all those conduits/flex to terminate on the enclosure.
 
You could use something like this with one on each side of the spade for 16 terminals.

But still don't understand how it's possible to come out of the xfrmr with 16 sets of 4". Does not seem like there would be enough room for all those conduits/flex to terminate on the enclosure.

Sorry I have 9 sets 4".
 
But still don't understand how it's possible to come out of the xfrmr with 16 sets of 4". Does not seem like there would be enough room for all those conduits/flex to terminate on the enclosure.

Sorry I have 9 sets 4".
Typically on a a pad mount transformer they don't actually terminate ... they just stub up in an open bottom. Pad mount or not, you would have to look at the actual transformer drawings to see what room is available for conduits.
 
Is this transformer a POCO transformer?

If so, you should have their book of standards which has every type of xfmer they use with drawings and specs

Is this transformer one that was furn/installed by a contractor?

If so, manufacturer name, cat# and order number can all be looked up.....
 
Is this transformer a POCO transformer?

If so, you should have their book of standards which has every type of xfmer they use with drawings and specs

Is this transformer one that was furn/installed by a contractor?

If so, manufacturer name, cat# and order number can all be looked up.....

Not a POCO. We, the EC, are F&I.
 