All of the outfits I have done work for (major Industrial) specify a green wire egc in each conduit.. If there is flex, they spec a green wire external jumper.
I agree. Conduits do crack (at the fittings) and a flex is not much of an egc.
One issue I have run into at an older mill was with deteriorating conduits. The mill was a cadilac job when it was new. But no green wire EGC in the MCC feeders. Fast Forward 25 years. MCCs would develop an arcing ground fault, but with a compromised conduit EGC path, the current would not build quickly. The ground fault would burn away for several cycles until it went phase to phase - then it would trip quickly. In the meantime the faulted MCC was a real mess. No way was the mill ever going to rip out all the major electrical and rebuild.
I call GE and tell them I've got a slug of 1960s vintage, 600A, AK-25s . Do they have a retro fit trip unit that will monitor GF?
"Oh yeah. We got a Micro-Versa-Diga-Flux-fixall" trip unit replacement kit. We developed it for all the old mills that didn't pull a green wire ground. Arcing ground faults are burning up the MCCs that are not trippng quickly on GF and are burning up the MCCs before the phase to phase kicks in."
Ahhhh. Budget price, lead time, please.
So, I like a green wire ground and so do my customers. Is it better than a good conduit - No but they feel better seeing a fat wire in the lug in the connection boxes.
And most are going with MC-HL now, so this is getting to be a moot issue. But it is still in their specs - if conduit, then green wire.
ice
I agree. Conduits do crack (at the fittings) and a flex is not much of an egc.
One issue I have run into at an older mill was with deteriorating conduits. The mill was a cadilac job when it was new. But no green wire EGC in the MCC feeders. Fast Forward 25 years. MCCs would develop an arcing ground fault, but with a compromised conduit EGC path, the current would not build quickly. The ground fault would burn away for several cycles until it went phase to phase - then it would trip quickly. In the meantime the faulted MCC was a real mess. No way was the mill ever going to rip out all the major electrical and rebuild.
I call GE and tell them I've got a slug of 1960s vintage, 600A, AK-25s . Do they have a retro fit trip unit that will monitor GF?
"Oh yeah. We got a Micro-Versa-Diga-Flux-fixall" trip unit replacement kit. We developed it for all the old mills that didn't pull a green wire ground. Arcing ground faults are burning up the MCCs that are not trippng quickly on GF and are burning up the MCCs before the phase to phase kicks in."
Ahhhh. Budget price, lead time, please.
So, I like a green wire ground and so do my customers. Is it better than a good conduit - No but they feel better seeing a fat wire in the lug in the connection boxes.
And most are going with MC-HL now, so this is getting to be a moot issue. But it is still in their specs - if conduit, then green wire.