Saw this comment on Reddit
"the mechanical terminals for most residential devices are not rated for stranded wire".
True or not?
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I believe he was referring to the screw terminals on a switch or receptacle device. It was a discussion about why stranded wire is not widely used in residential work.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'd have to do some digging for the accuracy of this, but I say this is not true. Seems like I or we here have been down this road before.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
You will find your ansawer in the UL white book.
Look at recpt and snap switch. You may find it interesting.
Also check the instructions for the devices your using.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
I had this issue with an AHJ.
Here is what I sent him.
They were trying to enforce crimps.
In our case they no amendment stating such use and there was no job spec.
 

Attachments

  • Screenshot_20230127-054505.png
    Screenshot_20230127-054505.png
    341 KB · Views: 51
  • Screenshot_20230127-054349.png
    Screenshot_20230127-054349.png
    565.6 KB · Views: 49

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Since I mentioned it.
 

Attachments

  • Screenshot_20230127-055702.png
    Screenshot_20230127-055702.png
    493.5 KB · Views: 33
  • Screenshot_20230127-055848.png
    Screenshot_20230127-055848.png
    137.5 KB · Views: 33

kwired

Electron manager
Location
NE Nebraska
You will find your ansawer in the UL white book.
Look at recpt and snap switch. You may find it interesting.
Also check the instructions for the devices your using.
I know this topic comes up every once in while on this site. The answer always is nearly all of the can be used with stranded conductors, and IIRC the white book almost always was mentioned as a reference on this.
 

dkidd

Senior Member
Location
here
Occupation
PE
UL RTRT

Terminals of the wire-binding screw, setscrew, or screw-actuated back
wired clamping types are suitable for use with both solid and stranded
building wires.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
So stranded for receptacles yes, switches no unless marked for use with.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician

VirutalElectrician

Senior Member
Location
Mpls, MN
Occupation
Sparky - Trying to be retired
I believe "back stab" type contacts are NOT rated for stranded wire. As the clamping mechanism would force the strands to spread out and not clamp properly. But it's been a long time since I installed a back stab capable device. They are generally low end devices.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
I know this topic comes up every once in while on this site. The answer always is nearly all of the can be used with stranded conductors, and IIRC the white book almost always was mentioned as a reference on this.
Good to know thanks.
I will do a search and read out of curiosity.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I believe "back stab" type contacts are NOT rated for stranded wire. As the clamping mechanism would force the strands to spread out and not clamp properly. But it's been a long time since I installed a back stab capable device. They are generally low end devices.
1. Some back wired receptacles actually clamp onto the back wire using the side terminal screws to compress an internal clamp. Not actually back stab.
2. Where there is an issue with stranded wire is that most terminals that accept stranded wire do not allow use of fine stranded wire. Generally not an issue in residential wiring though.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I’ve always differentiated the two by terms “back-wired” vs “back-stabbed.” I’m not sure how pervasive that distinction is.
Industry slang often gets in our way.😀

UL calls these back-wired and 'push-in' according to the info in post #6, above.
 

kwired

Electron manager
Location
NE Nebraska
UL makes a point of stating receptacles can use solid or stranded but switches have to specifically be marked for stranded in order to use the wire binding type terminations for stranded conductors.
Wonder why? Not really much for construction differences in the components that matter here.

I've been using stranded conductors on both for many years and almost never had any problems. More recently have gone mostly to "back wired" devices with the pressure plate terminals, and is faster install IMO for both solid and stranded.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
Some pics
 

Attachments

  • Screenshot_20230128-091841.png
    Screenshot_20230128-091841.png
    158.1 KB · Views: 5
  • Screenshot_20230128-091719.png
    Screenshot_20230128-091719.png
    64.1 KB · Views: 5
  • Screenshot_20230128-091408.png
    Screenshot_20230128-091408.png
    96.2 KB · Views: 4
  • Screenshot_20230128-091308.png
    Screenshot_20230128-091308.png
    79 KB · Views: 5
  • Screenshot_20230128-090952.png
    Screenshot_20230128-090952.png
    25.7 KB · Views: 5
  • Screenshot_20230128-090906.png
    Screenshot_20230128-090906.png
    150.3 KB · Views: 6
Status
Not open for further replies.
Top