When discussing short circuit coordination studies a topic of conservation came up and was looking for other opinions, when drawing a one-line in a modeling software some of my co-workers expressed that to get it done from a S.C. prospective they will indicate a feeder to a fuse and to the bus (switches and fuses are two pieces of equipment in this software) and omit the switch saying it is just another item to keep track of and adds time, however a switch has a specific x/r impedance etc. correct? To test this out I modeled the same system with the same characteristics and found that when the xfmr secondary feeder is connected to a switch and then a fuse and then the bus the fault current at the line side of the switch is approx 34ka while the fault current at the bus is approx 30Ka, when it is run with just the fuse and no switch in the circuit the approx fault current at the bus is approx 31Ka while if you omit the switch and fuse completely it is only decreased by the impedance of the cable but would be 35Ka all the way thru, is the decrease due to the impedance in the switch and fuse? It drops the fault current about 4Ka just passing thru the switch and fuse.